[rescue] E250 temperatures
Ron Wickersham
rjw at alembic.com
Sat Apr 12 16:04:18 CDT 2008
On Fri, 11 Apr 2008, Joshua Boyd wrote:
> I just noticed that the thermal error light was lit on my e250 running
> solaris 10. A quick login, and prtdiag shows:
> System Temperatures (Celsius):
> ------------------------------
> CPU0 64 WARNING
> CPU1 47
> MB0 41
> MB1 31
> PDB 35
> SCSI 29
just checking my system:
System Temperatures (Celsius):
------------------------------
CPU0 41
CPU1 44
MB0 34
MB1 29
PDB 28
SCSI 25
> Yet, the fans still aren't full speed:
> Fan Bank :
> ----------
>
> Bank Speed Status
> (0-255)
> ---- ----- ------
> SYS 219 OK
Fan Bank :
----------
Bank Speed Status
(0-255)
---- ----- ------
SYS 171 OK
so i show a slower fan and lower temperatures. i've been worried that
my room temperature is too high at around 75-degrees F, but have never
gotten a temp warning light in the five years this machine has been running.
this machine is not mounted in a rack, just sitting on the floor, in the
stand-up position and has another E250 on the top of it.
i am running both power supplies and 3 disk drives.
========================= CPUs =========================
Run Ecache CPU CPU
Brd CPU Module MHz MB Impl. Mask
--- --- ------- ----- ------ ------ ----
SYS 0 0 400 2.0 US-II 10.0
SYS 1 1 400 2.0 US-II 10.0
========================= Memory =========================
Interlv. Socket Size
Bank Group Name (MB) Status
---- ----- ------ ---- ------
0 none U0701 128 OK
0 none U0801 128 OK
0 none U0901 128 OK
0 none U1001 128 OK
the two CPUs are the same...are your CPUs different? this machine
is running Solaris 10 with 12 zones and in some of the zones there
are 20 virtual hosts of apache, and some heavy usage in perl scripts
for bulletin board system called Discus, so the perfmeter frequently
shows both CPUs maxed out and the load average up to ten so the
machine isn't just sitting idle.
when you have the machine apart, i'd check that all three fans are
putting out the same volume of air, feeling the flow with your hand
should be adequate for that. i could imagine that if one fan were
running slower then the lower airflow could make a difference on the
parts cooled by it.
> What is the real danger region for the E250, and will the light turn off
> on its own if the temp goes down?
>
> Also, does anyone know any tricks to make it balance the thermal load
> between the two CPUs better?
what kind of computational load are you running?
> Any other tricks? I would venture to say that the area where the E250
> sits is still generally under 70 degrees.
this is cooler than the external temperature that my machine is running
in.
> The e250 is near the bottom
> of a short rack that doesn't actually have all that much running in it.
that should be the coolest place in the rack
> Below the e250 is a smartups 1400.
is the e250 laying down in the rack-mount orientation or standing up in the
"normal" orientation shown in the product pictures? and assuming that
you have the side panels on the e250 which make the airflow go the way
intended by the design.
> The only things running above it are
> a SS20, a GigE switch, and a FastE switch (the FC array, T1, and Compaq
> DL360 are off). On top of the rack is a Ultra 5, and a few feet away is
> an Ultra 80, which doesn't seem to have the same sort of monitoring on
> it. I may have to get a remote device to monitor the area...
in feeling the e250 there is no warmth from anyside of the side panels,
the airflow keeps the case absolutely at room temperature. so i can't
imagine that any gear either above or below would affect its temperature
in any measureable way.
-ron
More information about the rescue
mailing list